Hi all, I have some results I can't explain. More than happy for it to be a conceptual misunderstanding on my part. I came across it with a different model but get the same behaviour with the simplified model discussed below: My base model has one compartment 50m x 50m x 10m (WLH) with a constant fire output of 5MW running for 1 hour. The difference between the two is that the first model has no leakage at all, where as the the second has leakage at a rate of 0.0012m2/m2 over the walls. There are no material properties set so the model should be running as adiabatic. I have also tried this with ticking the adiabatic option and get the same results. The model without leakage reaches an UL peak of 845oC and the model with leakage gets to 1,180oC. The LL temps are similar. I expected the leakage model to have a lower temperature. Tracking enthalpy, the no leakage model matches with what I would expect, but obviously the leakage model does not. See attached png. I would expect enthalpy exchange through the vent with net outflow so the average temperature in the compartment should go down. The actual HRR is as expected and the compartment size has enough oxygen above the limit to sustain the fire for at least 1 hour. So, the no vent case is not underventilated and introduction of a vent does not allow more energy release in the compartment in this case. If my working out is right, the temperature in the leakage case defies energy conservation. Again, more than happy to be shown the error of my ways here. Note that I have also tried running the model manually inputting the wall vent rather than relying on the leakage input (sill at 5%, total height at 90% of compartment height). The results were the same. So, what am I missing? Thanks in advance. Input files are below: &HEAD VERSION = 7700, TITLE = 'TA1_NoVenting' / !! Scenario Configuration !! Compartments !! Fires &TAIL / &HEAD VERSION = 7700, TITLE = 'TA2_venting' / !! Scenario Configuration !! Compartments !! Fires &TAIL / |
Beta Was this translation helpful? Give feedback.
Replies: 4 comments 2 replies
-
Leakage is treated as a narrow vent. Look at the flow and hrr outputs. You
will eventually have bi-directional flow in the leak path and the hrr that
results will far outweigh the cooling effects of the air exchange.
…On Tue, Oct 24, 2023, 12:13 SFC-CA ***@***.***> wrote:
Hi all,
I have some results I can't explain. More than happy for it to be a
conceptual misunderstanding on my part. I came across it with a different
model but get the same behaviour with the simplified model discussed below:
My base model has one compartment 50m x 50m x 10m (WLH) with a constant
fire output of 5MW running for 1 hour. The difference between the two is
that the first model has no leakage at all, where as the the second has
leakage at a rate of 0.0012m2/m2 over the walls. There are no material
properties set so the model should be running as adiabatic. I have also
tried this with ticking the adiabatic option and get the same results.
The model without leakage reaches an UL peak of 845oC and the model with
leakage gets to 1,180oC. The LL temps are similar. I expected the leakage
model to have a lower temperature. Tracking enthalpy, the no leakage model
matches with what I would expect, but obviously the leakage model does not.
See attached png. I would expect enthalpy exchange through the vent with
net outflow so the average temperature in the compartment should go down.
The actual HRR is as expected and the compartment size has enough oxygen
above the limit to sustain the fire for at least 1 hour. So, the no vent
case is not underventilated and introduction of a vent does not allow more
energy release in the compartment in this case.
[image: Enthalpy]
<https://user-images.githubusercontent.com/52268149/277529998-b4e0689d-0938-4b97-affb-85253a40565e.png>
If my working out is right, the temperature in the leakage case defies
energy conservation. Again, more than happy to be shown the error of my
ways here.
Note that I have also tried running the model manually inputting the wall
vent rather than relying on the leakage input (sill at 5%, total height at
90% of compartment height). The results were the same.
So, what am I missing? Thanks in advance.
Input files are below:
------------------------------
&HEAD VERSION = 7700, TITLE = 'TA1_NoVenting' /
!! Scenario Configuration
&TIME SIMULATION = 3600 PRINT = 60 SMOKEVIEW = 15 SPREADSHEET = 15 /
&INIT PRESSURE = 101325 RELATIVE_HUMIDITY = 50 INTERIOR_TEMPERATURE = 20
EXTERIOR_TEMPERATURE = 20 /
!! Compartments
&COMP ID = 'Comp 1'
DEPTH = 50 HEIGHT = 10 WIDTH = 50
ORIGIN = 0, 0, 0 GRID = 50, 50, 50 /
!! Fires
&FIRE ID = 'New Fire 1' COMP_ID = 'Comp 1', FIRE_ID = 'New Fire 1'
LOCATION = 25, 10 /
&CHEM ID = 'New Fire 1' CARBON = 1 CHLORINE = 0 HYDROGEN = 4 NITROGEN = 0
OXYGEN = 0 HEAT_OF_COMBUSTION = 50000 RADIATIVE_FRACTION = 0.35 /
&TABL ID = 'New Fire 1' LABELS = 'TIME', 'HRR' , 'HEIGHT' , 'AREA' ,
'CO_YIELD' , 'SOOT_YIELD' , 'HCN_YIELD' , 'HCL_YIELD' , 'TRACE_YIELD' /
&TABL ID = 'New Fire 1', DATA = 0, 5000, 0, 0.09, 0, 0, 0, 0, 0 /
&TABL ID = 'New Fire 1', DATA = 3600, 5000, 0, 0.09, 0, 0, 0, 0, 0 /
&TAIL /
------------------------------
&HEAD VERSION = 7700, TITLE = 'TA2_venting' /
!! Scenario Configuration
&TIME SIMULATION = 3600 PRINT = 60 SMOKEVIEW = 15 SPREADSHEET = 15 /
&INIT PRESSURE = 101325 RELATIVE_HUMIDITY = 50 INTERIOR_TEMPERATURE = 20
EXTERIOR_TEMPERATURE = 20 /
!! Compartments
&COMP ID = 'Comp 1'
DEPTH = 50 HEIGHT = 10 WIDTH = 50
ORIGIN = 0, 0, 0 GRID = 50, 50, 50 LEAK_AREA_RATIO = 0.0012, 0 /
!! Fires
&FIRE ID = 'New Fire 1' COMP_ID = 'Comp 1', FIRE_ID = 'New Fire 1'
LOCATION = 25, 10 /
&CHEM ID = 'New Fire 1' CARBON = 1 CHLORINE = 0 HYDROGEN = 4 NITROGEN = 0
OXYGEN = 0 HEAT_OF_COMBUSTION = 50000 RADIATIVE_FRACTION = 0.35 /
&TABL ID = 'New Fire 1' LABELS = 'TIME', 'HRR' , 'HEIGHT' , 'AREA' ,
'CO_YIELD' , 'SOOT_YIELD' , 'HCN_YIELD' , 'HCL_YIELD' , 'TRACE_YIELD' /
&TABL ID = 'New Fire 1', DATA = 0, 5000, 0, 0.09, 0, 0, 0, 0, 0 /
&TABL ID = 'New Fire 1', DATA = 3600, 5000, 0, 0.09, 0, 0, 0, 0, 0 /
&TAIL /
—
Reply to this email directly, view it on GitHub
<#2063>, or unsubscribe
<https://github.com/notifications/unsubscribe-auth/ADBUZ4O66H5KFOAIAYXM7I3YA4W7PAVCNFSM6AAAAAA6NAQ2UKVHI2DSMVQWIX3LMV43ERDJONRXK43TNFXW4OZVG43TANBVGY>
.
You are receiving this because you are subscribed to this thread.Message
ID: ***@***.***>
|
Beta Was this translation helpful? Give feedback.
-
The internal energy of the sealed compartent is dP V_0 + rho_0 V c dT. Your pressure in the sealed compartment is rising by 290 kPa. Alot of the fire energy (about 40 %) is going into raising the pressure. Ignoring the energy loss from the vent outflow, you would expect 60 % of the temperature rise in the sealed case vs. the open. The actual value is 70 % but loosing 10 % of the energy from the leakage flow doesn't seem unreasonable. |
Beta Was this translation helpful? Give feedback.
-
The quantity you are conserving in sealed volume is internal energy (U): U = rho_0 V_0 c_p dT - dP V_0 = rho_0 V_0 c_v dT when you use constant volume specific heat you are accounting for pressure with that. |
Beta Was this translation helpful? Give feedback.
-
OK, that's what I thought. I still need to convince myself of the sealed vs non-sealed case, though. Thanks for your help, Jason. Much appreciated. |
Beta Was this translation helpful? Give feedback.
The internal energy of the sealed compartent is dP V_0 + rho_0 V c dT. Your pressure in the sealed compartment is rising by 290 kPa. Alot of the fire energy (about 40 %) is going into raising the pressure. Ignoring the energy loss from the vent outflow, you would expect 60 % of the temperature rise in the sealed case vs. the open. The actual value is 70 % but loosing 10 % of the energy from the leakage flow doesn't seem unreasonable.