Hey @hanskroner - I have another case study!

In #1678 the user reports that he has 4 identical devices of which 1 reports its state automatically and 3 don't. All of them support Z-Wave+ CC V2, so they should be required to report instantly. All of them have the same association config, all of them are in short range to the controller.

Z-Wave Plus v2 does indeed require Multi-level Switches to send a MULTILEVEL-SWITCH_REPORT to the Lifeline when the multi-level value changes - but only once the device has reached the final state.

The only difference I could find is that the one that does report is not included securely, all others are communication with S0 encapsulation.
At a first gla…

Replies: 1 comment

Comment options

You must be logged in to vote
0 replies
Answer selected by AlCalzone