Three-phase fault at desired line position, some strange TDS results #386
-
Based on Case 1: Load factor 100%, fault occurs in line_12 at 80% positon during 1.0s~1.3s Below is TDS result:
Case 2: Load factor 100%, fault occurs in line_12 at 90% positon during 1.0s~1.3s Below is TDS result:
Case 3: Load factor 100%, fault occurs in line_12 at 95% positon during 1.0s~1.3s Below is TDS result:
Problem:
|
Beta Was this translation helpful? Give feedback.
Replies: 3 comments
-
Looks like your case 2 is not properly initialized. You will need to adjust the limits of some turbine governors and exciters accordingly. For case 3, it's not due to the fault. Double check if any other parameters are modified or lines are accidentally removed. |
Beta Was this translation helpful? Give feedback.
-
Hi, I will take a look at this issue and expect a response within one week. Regards, |
Beta Was this translation helpful? Give feedback.
-
Hi, After investigation, the failure of Case2 and Case3 are caused by inappropriate parameters. Case2 is caused by the limiter value, and Case3 is caused by the Bus initial voltage and angle. More details can be found in the attached PDF. Regards, |
Beta Was this translation helpful? Give feedback.
Hi,
After investigation, the failure of Case2 and Case3 are caused by inappropriate parameters.
Case2 is caused by the limiter value, and Case3 is caused by the Bus initial voltage and angle.
More details can be found in the attached PDF.
Regards,
Jinning
Discussion386.pdf