Hi,
I spent some time reverse engineering my Buderus Logavent HRV156 over EMS-ESP. The exhaust fan on my unit was running much too slow on L1/L2. I found several telegrams that EMS-ESP does not support yet. Two of them are writable parameters that would make useful entities, among them the volume flow balance that is normally only available in the RC310 service menu. The current ventilation support comes from #1172 and #2038, so I'm posting this as a follow-up.
Setup
Method
watch onwhile switching levels L1–L4/off viaventmode, plus periodicread 51 <type>system/send(EMS+ format0B 51 FF <offset> <typeH-1> <typeL> <data>): one byte at a time, small change, read back, observe for 10–60 s, then restore the original value and verify itWritable parameters (verified)
0x64). The device accepts up to 110; writing 120 is limited to 110. Affects only the exhaust fan, supply stays constant. This matches the RC310 service menu item "Volumenstromabgleich 90–110 %, Abluft variabel, Zuluft konstant".L3 seems fixed at 100 % (= nominal volume flow, RC100 H service item U.2). 0x0561 off 18/19 had no effect at L3.
Read-only values (verified by level changes)
Level table from my unit (same control voltage for both fans; the exhaust fan has a start-up problem, see below):
Not writable (status only)
0x0575, 0x0585, 0x0587, 0x0586 (
00 64 64, probably the effective balance factors) and 0x055D off 0 / 0x055E off 3–9. Writes are accepted on the bus but the read-back shows the old value and nothing changes.ventmodeback fixes it.Many other bytes in 0x0556, 0x055B, 0x055D, 0x055F, 0x0560, 0x0565 and 0x0566 are writable but showed no visible effect at fixed levels. They probably belong to other modes, the filter interval, frost protection and similar. I restored them all and did not decode them.
Suggestion for EMS-ESP
New entities for ventilation:
ventBalance/ "volume flow balance exhaust" (0x0556 off 8, %, writable, range probably 90–110)level1Pct,level2Pct,level4Pct(0x0561 off 14/15/13, %, writable)ventOutRpm/ventInRpm(0x0583 off 2/17, uint16)ventOutVoltage/ventInVoltage(0x0587 off 2/4, uint8 /10, V)The rpm values are very useful for diagnostics. On my unit you can see directly that the exhaust fan sometimes doesn't start at L1/L2: it stays at ~300–360 rpm while the supply fan runs at ~2900 rpm with the same control voltage. It only starts when you go through L3/L4 first.
Happy to test a dev build or provide more logs
All reactions