Do many (even disabled) loadpoints slow down evcc's control cycle? #36388
Unanswered
rolfste
asked this question in
Need help?
Replies: 3 comments
|
What you're seeing comes from how the loop works. I checked
So the practical lever is fewer loadpoints, not a shorter interval. Below 30s evcc already logs a warning. Remove seasonal devices from the config while they're unused, since there's no "exclude from loop" flag. If several small heaters only ever switch together, consider merging them into one switchable loadpoint. |
0 replies
|
Best solution would be, if the long promised "Mini Loadpoints" #7235 would be realized. |
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
Description
I run evcc (v0.319.1, linux/arm64) with 16 loadpoints. Besides the wallbox, most of them are small consumers (heating rod/AC-THOR, convector heaters, air conditioners, battery chargers, a home battery cluster, etc.), most of them connected via Home Assistant. Many of these loadpoints are in mode "off" most of the time and are only switched to "smart" by Home Assistant when needed.
I reduced the interval from 30 s to 10 s because I noticed that some loadpoints (e.g. the heating rod) were only adjusted roughly every 7–8 minutes when PV surplus changed. My impression is that evcc does not adjust all loadpoints in every cycle and that the reaction time grows with the number of loadpoints.
My questions:
I can provide configuration and debug logs if needed.
Steps to Reproduce
Version
v0.319.1
System
linux/arm64, CET +01:00