KOSTAL PLENTICORE G1: Does enabling Battery:ComMonitor:Enable fix Modbus handback for others? #36537
Unanswered
stegm
asked this question in
Need help?
Replies: 1 comment 3 replies
|
Is not known, yet. afaik. It would be good to know the flag is persistent. |
3 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
The KOSTAL PLENTICORE wiki notes that some older inverters don’t reliably return to internal battery control after external Modbus commands stop. I had this problem on a PLENTICORE plus 10 G1 (UI 01.30.12092, MC/IOC 01.80, BYD battery, evcc 0.319.0).
I had the exact described problem. When I started external control, the inverter does not return to internal if the external control stopped.
I then changed only
Battery:ComMonitor:Enablefrom 0 to 1 using pykoplenti with installer credentials:After that, the inverter takes back control when no more external commands where given. The manual
evcc meter verifybatterymodestest worked also. I haven’t tested whether the flag survives a power cycle yet.Does anyone else with this symptom want to try it? It would be helpful to know your inverter model and firmware, whether
Battery:ComMonitor:Enablewas 0 before the test, and whether the battery actually resumes normal self-consumption after the change. Reports where the flag is already 1 or enabling it doesn’t help are useful too.If others can reproduce the fix, I’m happy to update the wiki with the diagnostic check and the workaround.
All reactions