Same here, when using the solar production it's adding this to the home use, which is incorrect because this PV power used for charge. There is a value for PV to the battery and PV to the home. And "Pv to the Home" should be used as solar production within Omnibattery I've now combined Gielz Zendure integration which adds PV to the Home as entity and used that in Omnibattery for solar production but this is not a nice permanent solution. Please add the Zendure PV-in and PV to the home to the zendure entities within omnibattery. I think that these are the api fields |
|
Thanks both. Right now the SolarFlow 4000 Mix AC+ is treated as a pure AC-coupled battery: the integration doesn't expose Before adding it I need to confirm what those fields actually report on the AC+ (I don't want to double-count solar that's already in another reading). Could one of you share an anonymised
The fields I care about: A quick note on the wiring would also help: where the three PV inverters and the grid meter sit relative to the SolarFlows. |
|
gridOffPower2 is the power from PV on the PV-in AC. The amount is the same as in the zendure app. |
|
Same issue with the Mix 3000 AC+ Idem: je ontlaadt de accu EN je hebt een verbruiker op de off-grid poort, dan worden beide vermogens onttrokken uit de accu en je kunt boven het limiet van 3680 W komen. Niet wenselijk. Ontlaadstroom naar het net c.q. huis moet dan beperkt worden. Verder: is het mogelijk om het vermogen van de off-grid poort zichtbaar te maken in het dashboard? |
|
Thanks @gjburg and @stopie82, that report helped a lot. Right now the AC+ is handled as a pure AC battery, so the PV coming in on PV-in AC ( Before I wire
It would also help to know where the PV inverter and your grid meter sit relative to the SolarFlow. A rough sketch is fine. @sailor22, could you send one report taken during forced charge with PV on the off-grid port? I want to see whether the firmware already caps grid + PV at |
|
@ffunes i cannot provide it for the coming 2 weeks due to holiday. After that i can do it |
|
Hello, |
|
@ffunes I've logged the local API ( Setup
Key fields
Full (anonymised) reports for each case are attached. Observations
What would help in OmniBattery
Happy to run more tests or log other fields if that helps. |
|
@ffunes need more information for the integration? Do you have any rough forecast? |
|
Thanks all, @FutureCow's logs settled it. PV-IN AC support is in for 2.0.0: on a 3000/4000 Mix AC+ with If your Solar Production sensor already includes the PV-IN inverter (an SMA sensor, or the Gielz workaround), take it out after updating, or it will count twice. Two things I still can't check from the reports so far:
Feeding the house from the battery while PV-IN charges it (NOM) is a separate change; I'll look at it once this is confirmed in use. |
|
I hope I can answer 1 today, there is some sun filling the battery at this moment! |