Common issues with comfort schedules
It's very hard for a heatpump to make up 1-2c differences between hours. In this example the base diff between 08:00 and 09:00 is 2c.
Too narrow area below the base. It's also an imbalance. You are basically telling the optimizer to stay above the base this way. It's advised to make more balance band (see below). If you really want this schedule, then lower the kwh penalty to allow going below the base
Simple but effective schedule
0.10.30.51.02.0Recommended schedule
Check your heatpump Max kW output and Max flow temp
If your climate is colder, then pick the rows above. Basically get the max at the design temperature.
Set the max flow temp to restrict too high flow temps. For underfloor heating around 32c is probably fine. Try and see at what max temp your heatpump is operating without having to go all-in.
for the smaller SUZ units, try to maintain a delta T of around 3c. The units will go max if the delta T is too high