How-to: emulate a VR 92 remote with ebusd to feed an external room temperature into a sensoCOMFORT (VRC 720 / CTLV3) #1833
mruessler
started this conversation in
Show and tell
Replies: 0 comments
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
Writing
Z1RoomTemp(orz1RoomTemp) into a sensoCOMFORT is a recurring question here (e.g. #707).The register accepts the write, but the value is gone within a second and the controller doesn't regulate on it.
What does work is to make ebusd be a VR 92 remote control and send the room temperature the way a real remote does.
The controller then regulates the assigned zone on that value.
Tested on one system for a few hours. Treat it as an experiment, not a finished feature.
Tested setup
CTLV3, SW 0808 / HW 8004, slave15Background: VR 92, not VR 91
The VRC 720 works with the VR 92 remote (the installation manual allows up to 4). The VR 91 belongs to the
older multiMATIC VRC 700. ebusd's CSV still calls the zone assignment value
VR91_1, but that's only a labelfor "Remote control 1". A fake VR 91 is identified by the VRC 720, but it is never talked to.
A real VR 92 identifies as
MF=Vaillant;ID=VR_92;SW=0514;HW=1204. Remote 1 uses slave35/ master30,remote 2 uses
75/70(see #1480).Step 1: run ebusd as master 30
The remote has to send from its own master address, so ebusd itself takes the remote's address:
ebusd's own slave address is then
35. Make sure no real remote uses 30/35.Step 2: answer the identification request
The controller only scans for remotes at certain times. On my system it did a full scan about 40 s after
ebusd started; a broadcast
07 feorscan 15did not trigger one. Runtime answers are lost on every restart,so register the identity right after ebusd has acquired the signal:
In the log you should see the controller (
10) accept it:The controller display now lists "Remote 1 (5.14)", and the app shows
F.5056 "Assignment of remote control 1 missing".
Step 3: assign the zone
On the controller, set the zone assignment of the zone to Remote 1
(
Z1RoomZoneMapping = VR91_1in ebusd terms), and set room temperature control of thecircuit to Active (
modulating) or Extended (thermostat). F.5056 disappears.Step 4: send the room temperature
Each remote has its own register block in the controller:
b524group0a, instance = remote number.Register
0fis the room temperature (float, little endian). The remote writes it with opcode06 01:Convert any temperature, e.g. with Python:
The value sticks: register
0fandZ1RoomTempkeep it (I refresh every 60 s, like a real remote probably would).Proof that the controller regulates on it
With 18 °C pushed, zone in "Extended" (thermostat) mode:
vr_71 Mc1Operation on;30.5;…)Mc1Operation off;0.0(room 18 > target 17)With an empty room temperature the circuit would just keep heating on the weather curve.
Remote register block (group 0a, instance 01) as seen on my system
Read with
ebusctl hex 15b5240606000a01RR00. Empty floats readffffff7f.02350405 0e070f30Limitations
06 01 0a 01 30 00 0band02 01 03 00 14 00 <float>(the zone target). ebusd can't ACK these:
answernever matches requests with more than 4 data bytes(issue: answer never matches requests with more than 4 data bytes (negative shift in DirectProtocolHandler::getAnswer()) #1832 ). The controller retries 3× and carries on; I haven't seen any errors from this so far.
(the circuit then heats on the weather curve). After every ebusd restart, register the answer again
before the controller's scan.
whether remote 2 works the same way (
-a 70, slave75, instance02), and whether the humidity registeris used.
To undo
Set the zone assignment back to the controller, then remove
-a 30and restart ebusd.Unofficial and at your own risk. Feedback from anyone with a real VR 92 who can capture what it sends
(
ebusctl raw, look for telegrams from30) would help a lot.All reactions