Thanks. 9051 is the same board family as 5190, another Hybrid, which is mapped for the meter and the counters only: nobody has placed the targets on it yet. A memory dump would tell. Diagnostics → Memory read, From 0x0800 To 0x2FFF, then Dump and Download (nothing is written to the unit), taken while the interface shows known values: note your leaving water curve (the four numbers of [1-00] to [1-03]), the hot water setpoints and the leaving water target the home screen shows at that moment. Attach the file here. #712 is a good example of what helps. |
|
Thanks! Two dumps attached, taken on 24.11.2026 around 17:35 (Europe/Berlin):
Values on the user interface at that time:
What I noticed (hope it helps):
Unit: EHYHBH05AAV3, hydro board software 9051, ESPAltherma 2.0.0-beta.34, definition Altherma(Hybrid).h. |
|
Thanks, the two dumps were enough: 9051 is mapped in beta.35, out now. It is the layout of the 2014-2017 boards, moved. Your hot water curve reads 52 / 52 at 0x15E0 / 0x161E and your leaving water curve 35 / 50 at 0x15E2 / 0x1620, as temperatures × 256, which is why a search for whole numbers found nothing. Their ranges read 35..60, 45..60, 35..50 and 35..45, the leaving water target at 0x10C4 read 40.25 when your interface said 40.2, and the setting bytes are where they are on every board. The unit's own counters came with it, at the same place as on the other Hybrid software. In your dump: 10121 kWh of heat produced (9592 space heating, 530 hot water), 4110 kWh of electricity, 4616 h of compressor in heating and 107 h in hot water, 9227 h of pump, 24664 starts. Could you compare them with the interface's energy and operating hours screens? After the update, Settings → Experimental, tick the leaving water target, then in two steps:
Nothing was ever written on a 9051, you would be the first: step 1 first. |
Uh oh!
There was an error while loading. Please reload this page.
Hi, thanks for ESPAltherma 2 – it runs great on my hybrid.
The web interface shows "not available (hydro board software 9051)" for the
leaving water target. I would like to help add support for this board.
Unit:
Setup:
Reading works fine (incl. the 0x64 hybrid block: Hybrid Op. Mode,
Boiler Operation Demand, BE_COP …).
I'm happy to run a memory dump or test builds if you tell me what you need.
Thanks!