The hydro board does seem to hold a value close to it: your dump has a few places that read 1.7 while the boiler showed 1.7 bar, but one dump cannot tell them from chance. A second dump of 0x0800–0x2FFF at a clearly different pressure, with the figure on the boiler's display at that moment, will show which one moves. |
|
current water pressure on the gas boiler : 1.9 bar |
|
dropped water pressure on gas boiler : 1.5 bar increased water pressure on gas boiler : 2,0 bar |
|
@janlinders thanks, your two dumps settle it. One value in the hydro board's memory moved with the pressure: 1.45 when your boiler showed 1.5 bar, 2.02 at 2.0. On @bunni1310's dump the same place reads 1.80, with 1.7 on the display. (The first two files you attached are bunni1310's own, the 1.9 bar one included: only the 1.5 and the 2.0 ones are from your unit.) So the hydro board does receive the boiler's pressure, but not in a registry: the Water pressure of the definition will stay at 0 on the Hybrid. I added a value of its own, read from the board's memory once a minute: Boiler water pressure (bar), a pressure sensor in Home Assistant, the attribute of the same name on MQTT, and It is in a development build for the two of you to try before beta.36: System → Firmware update, tick Development builds, then Check for an update; it shows as What I would like to know after a few days: does it follow the boiler's display, and by how much does it differ? bunni1310's 0.1 is the one figure I cannot explain. The address was found by its value on your two units, not in the board's code, so your readings are what confirms it. One correction, @janlinders: the "5190" of your report and bunni1310's "9051" are the same software, the same two bytes read in the other order. The notes of beta.35 named two; my mistake, corrected in the same build. |
|
Thx Raomin, looks we are heading in the right way.
dump of 0x0800–0x2FFF espaltherma-memory-dump (4).txt
|
|
The Water Pressure on the boiler is now on 2.5 |
|
Thanks a lot – here are my results on dev-ead59ba (EHYHBH05AAV3, hydro board software 9051), 25.11.2026 around 15:00. Boiler water pressure Unit counters – compared with the interface (menu 6.2 and 6.7.D), all identical:
The interface also shows a "heat generator" counter (Wärmeerzeuger = the gas boiler): space heating 1552 h, tank 234 h, total 1786 h. It's not in ESPAltherma yet, in case it's useful. Leaving water target
So writing works on a 9051. Happy to test more if needed. |
|
One question for later: the entity shows ram_only: false. Is there a RAM-only mode on 9051, and how often can the target be written safely? I'd like to drive the target from Home Assistant every ~10 minutes eventually. |
|
RAM only tested on my 9051 (Experimental box ticked, target set from HA): Wrote 41: ram_only = true, held = 41, saved = −1, curve_orig 35/50 remembered. Works as described, thanks! |
|
Hot water target also tested on my 9051 (RAM only ticked): wrote 50 from HA, the DHW setpoint went from 52 to 50 within about 10 s, held = 50, saved stayed 52 (memory not written), curve_orig 52/52 remembered, range 45–60. Restored with the button afterwards. Note: effective already showed 50 before the write, I guess that's my reheat setpoint [6-0C] = 50? |
|
Thank you so much, raomin! I really want to say a big thank you, both for this great project and for your incredibly fast support. Within a few days, my 9051 went from "awaiting a first report" to fully supported: water pressure, unit counters, leaving water target and now the RAM-only mode. That's amazing work. ESPAltherma has given me insights into my hybrid system that I never had before, and it's already helping me tune my heating (cycling, hot water, boiler behaviour). Being able to control the leaving water target from Home Assistant without wearing out the unit's memory opens up a lot of possibilities. I'll keep an eye on the pressure readings and the boiler hours and report back if anything looks off. Happy to test anything else on my 9051 whenever it helps. Thanks again, and keep up the fantastic work! 🙏 |
|
One more observation: I tried to set [9-04] (LWT overshoot) from 1 to 3 on the interface. After confirming, the interface restarts and [9-04] is back at 1. I had reportedly set it to 3 on 23.11 as well, and today it showed 1 again. Could ESPAltherma be writing a settings block back to the unit (e.g. during the first leaving water write today, before I ticked RAM only)? Or can you see the [9-04] value in my dumps? RAM only is ticked now, so the ESP should not write to the memory anymore. |








Uh oh!
There was an error while loading. Please reload this page.
Hi, follow-up from my other thread (EHYHBH05AAV3, hydro board software 9051, ESPAltherma 2.0.0-beta.34, definition Altherma(Hybrid).h).
The "Water pressure" value from the Hybrid definition is constantly 0 on my unit (since the ESP was connected, ~2 days of history, never anything else).
On the hybrid, the space-heating water pressure sensor sits in the gas boiler module EHYKOMB33AA (S7 in the boiler wiring diagram), and the boiler display shows the pressure correctly: currently 1,7 bar.
The boiler talks to the hydro unit over the 2-core boiler communication cable (X5 on the boiler side).
Questions:
Attached: two memory dumps (0x0800–0x2FFF and 0x3000–0x5FFF) taken at 17:45 while the boiler display showed 1,7 bar.
I can take more dumps at a different pressure (e.g. after bleeding/refilling) if that helps to locate it.
espaltherma-memory-dump (1).txt
espaltherma-memory-dump.txt