Diff between the two dumps (heating WD curve, lower point 26 °C -> 27 °C): 0x32A6: 2E -> 2F (46 -> 47) The curve point seems to be stored as (temperature + 20) in one byte, |
|
Thanks, a before/after pair is exactly the right method. The problem is the range, and that one is on me: the page proposes 0x3000-0x5FFF, which is where the softwares from 2019 on keep their settings. Yours is from 2017 and keeps all of it below 0x3000. Your two files are empty from 0x3800 up, and the bytes that moved at 0x32A6 and 0x32C9 follow the setting but are not what the board computes its target from: those are 16-bit values, and none changed in that range. Could you send one more dump, From 0x0800 To 0x2FFF, with what the interface shows at that moment:
One dump is enough, nothing to change this time. Your software's successor, 17014006, is supported, and yours should have the same layout a few bytes away: the dump tells how many. It goes into beta.39. |
|
Thanks, that makes sense – and good to know that 2017 software keeps its settings below 0x3000. I'll take a new dump of 0x0800–0x2FFF and attach it here. Values on the unit at the time of the dump: Leaving water curve (weather-dependent, main zone):
Home screen:
Hot water (fixed setpoint mode):
Unit: outdoor ERGA08DVA, indoor EHVX08S23D9W, hydro board software 17014004, ESPAltherma 2.0.0-beta.37. If it would help, I can take a second dump after changing one of the curve points or the DHW setpoint, so you get a clean before/after pair in the right range. Glad to hear 17014006 is supported and that beta.39 should cover this one. Happy to test it as soon as it's out. |
Uh oh!
There was an error while loading. Please reload this page.
Hi, and thanks for the great project!
ESPAltherma 2.0.0-beta.37 shows "Not available on this unit (hydro board
software 17014004)" for Hot water target and Leaving water target. I'd like to
help add support for this software version.
Unit
ESPAltherma
Unit configuration
What I can do
so the curve addresses can be located
Memory dump (Diagnostics, read only): [attached / will add in a comment]
heating curve lower point 26degrees
espaltherma-memory-dump (1).txt
heating curve lower point 27degrees
espaltherma-memory-dump (2).txt
will this help?
Thanks!