So I finally got around to install the clamps and the EnergyMe, but I think I might have misunderstood what it does. The loads it reads differ alot from the smart grid meter and the energy consumption CSV remains empty. What I needed: a system that monitors 9 different groups/loads, spread over 3 phases. Currently I have just the 9 different 'load' groups clamped. I have not clamped any wires coming directly from the grid, since I am not interested in the EnergyMe measuring the total usage: the P1 port from the smart grid meter can be used for this. But is it possible to just measure 9 groups/loads? The Channel config says channel 0 is used as a voltage reference: does that mean it should also always have the 'grid' role? If so, does that mean using a 3Phase always need to be 3 grid roles? |
Replies: 1 comment 6 replies
|
Hi! You can measure loads only, and the channel 0 can be used for that as well. Make sure you select load as role for all the channels, and you select the right phase. Please update as soon as possible to version 2.0.3 as it fixes some important bugs on three phase measurements. Finally, you can monitor up to 16 unique channels, thus a maximum of 5 full three phase loads. Can you post some pictures of your setup to better understand why the values are wrong? |
Hi! You can measure loads only, and the channel 0 can be used for that as well.
Make sure you select load as role for all the channels, and you select the right phase. Please update as soon as possible to version 2.0.3 as it fixes some important bugs on three phase measurements.
Finally, you can monitor up to 16 unique channels, thus a maximum of 5 full three phase loads.
Can you post some pictures of your setup to better understand why the values are wrong?