NA Split Phase with Loads to N #216
|
Hi, Wanted to start off by saying thanks! Awesome project and just what I was looking for. I was able to order several completed PCBs and am in the process of getting everything installed; so far so good. I have a question regarding North American split phase branch loads. I noticed in the manual that for a 240V split phase branch, I am instructed to put a CT on just one of the hot legs and set phase to "Split Phase". I understand this would work for something like an oven where 99+% of the energy goes from L1 to L2 but what about a branch that is 240V (L1 + L2) but has some 120V devices that pull from L to N? For example, say I put the CT on L1 but a device on the branch is connected to L2 to N (120V), would the meter be able to read that load? Another example would be a sub panel fed from a 2 pole breaker (L1 + L2) but there are 120V branches in the sub panel that are split between L1 and L2 to N. One more example, the compressor on an HVAC system will be 240V but some of the other parts of the AC/heat pump will only be 120V connected from L to N. Is the meter able to measure these types of loads. I'm not an electrician/electrical engineer but I have a pretty good handle on electricity and it seems like the meter configured this way may be missing these loads, is that correct? Thanks for all your hard work on this! |
Replies: 1 comment 2 replies
|
Hi! Thank you very much :) The idea is: you connect the voltage supply to L (either L1 or L2) and N (so 120V); that is what the device will read as voltage. Then all single-phase loads get a clamp on the live or neutral cable, and the measurement will already be right. For split phase loads, like a AC system, you will connect one clamp only to one of the two phases, and set up split phase in the channel phase configuration. This will essentially double the power readings. All of this is in the assumption that there are no L1/L2/N loads under the same breaker, but as far as I understand, there aren't in NA. |
Hi! Thank you very much :)
The idea is: you connect the voltage supply to L (either L1 or L2) and N (so 120V); that is what the device will read as voltage.
Then all single-phase loads get a clamp on the live or neutral cable, and the measurement will already be right.
For split phase loads, like a AC system, you will connect one clamp only to one of the two phases, and set up split phase in the channel phase configuration. This will essentially double the power readings.
All of this is in the assumption that there are no L1/L2/N loads under the same breaker, but as far as I understand, there aren't in NA.