Does solaredge-modbus-multi integration support Dynamic Active Power capability?
SolarEdge inverters support Power Control protocol with compatible firmware such as the SE5000H. It is specifically intended for real-time solar curtailment by an external Energy Management System (EMS) ie HomeAssitant.
I am in Australia and this is particularly important in summer when the grid price goes negative and exporting energy costs the consumer. So when my batteries become full and we have a negative kWh/$ I must stop exporting.
My reading suggests the following Modbus register value process
Write 1 to F300 (Enable Dynamic Power Control).
Set F310 to a timeout, for example 10 seconds.
Set F312 to a sensible fallback (often 100%).
Write 70.0 (Float32) to F322.
The inverters will then limit total output to approximately 70% of rated power.
Important implementation details.
F322 is a Float32 value.
It occupies two consecutive Modbus registers.
It must be written using Modbus Function Code 16 (Write Multiple Registers).
The registers use SolarEdge's specified word order (little-endian word order for the 32-bit value).
Dynamic means this register is intended to be updated continuously by an EMS (HA). If you set Command Timeout = 10 seconds, then my controller should refresh F322 at least every 5 seconds (or faster). If updates stop, the inverter automatically reverts to the Fallback Active Power Limit configured in F312.
In my two-inverter system (2 xSE5000H) the intended approach would be:
Enable Dynamic Power Control on the lead SE5000H inverter.
Write the Dynamic Active Power Limit to the leader inverter.
The leader will broadcast the dynamic command to its follower(s) over the RS485 leader/follower network.
This is generally preferable to repeatedly writing to the persistent Active Power Limit register, because the dynamic registers are specifically designed for frequent, real-time updates by an EMS. No need to worry about registers wearing out flash memory :).