This is a good read to see if all the registers are the same as what is implemented. https://www.dth.net/solar/luxpower/modbus/EG4-18KPV-12LV-Modbus-Protocol.pdf
Note some important things:
software groups the registers into 40 groups of 0-39, 40-79, 80-119 and
so on. When querying 40 registers, the starting address must be 0 (0-39),
40 (40-79 ), 80 (80-119), it is not allowed to query registers across groups
at the same time, if you need to query the values of these registers 38-40,
because 38-39 is in the first group, 40 is in the second group, so it must
be divided into two query