'over_switch' Mode | How to setup VT for low temperature underfloor heating systems correctly? #1151
Replies: 4 comments
|
Hello, for underfloor heating with a very long inertia, you should set the cycle to a large value (15 min or 30 min) and have a minimum activation delay like 5 min. This is explain here: https://github.com/jmcollin78/versatile_thermostat/blob/main/documentation/en/tuning-examples.md#central-heating-gas-or-oil-heating Then VTherm will avoid to switch on/off too often and don't touch the valve for less than 5 minutes. Of course you can adjust this values to your case. |
|
Hello @jmcollin78, thank you for your prompt reply. Oh my god! I recall this brief section on central heating appliances for oil and gas. About a year ago, I saw this section quite by chance when I was trying out your ingenious VT HA integration for my seven DECT radiator thermostats. All seven have been running perfectly in ‘over_climate’ ever since. At the time, I read the lines, but I wasn't at all sure whether I would ever need these values and might have to change them. Please excuse me for being a bit stupid and ‘stealing’ your valuable time. Kind Regards |
|
Hello @jmcollin78, it's me again. I followed your advice and set the value to 30 minutes max right away, (cycle_min: 30). And I was surprised by the result. Even when the room temperature matches the target temperature, in my case 20.0 °C, the value of “power_percent” is not zero.
I expected that once the target temperature was reached, the valve would stop operating completely. Is there still an error in my configuration?
|


Uh oh!
There was an error while loading. Please reload this page.
Hello jmcollin78,
since this is my first time here, I first searched the existing discussion posts for a similar case, as recommended.
And I almost got lucky. Unfortunately, the discussion on “over_switch or over_climate? #924” only partially applies to my underfloor heating. Unfortunately, I can't find the answer to my questions there, or any tips I could follow.
Before I get to my question, I would like to add some additional information.
The water-based underfloor heating runs in “over_switch” mode, as described in the VT description:
'https://github.com/jmcollin78/versatile_thermostat/blob/main/documentation/en/over-switch.md#prerequisites'
The only and decisive difference between the description and my setup can be found at position 6.
Instead of the heater, I use a 230 V actuator (technical data: https://www.strawa.com/wp-content/uploads/2020/04/55-00507x_IS.pdf) that operates a valve. This allows warm water at a constant temperature of +40 °C to flow into the heating loops of the underfloor heating circuits – or not.
The actuator used has only two states: completely closed (0 volts) and completely open (230 volts).
It takes 180 seconds to move from completely closed to completely open.
The actuator therefore needs 360 seconds to complete the entire travel distance OFF → ON → OFF.
The actuator is also switched by a 230 V switch, as shown in the description.
In my setup, the switch is a “Wave 1 Mini” from Shelly for 230 V.
So what's my problem?
Could it be that the VT is optimized for electric radiators with an output in the range of several kW in the “over_switch” operating mode?
What settings would need to be made in Versatile Thermostat so that the switch (Shelly) could remain permanently in the ON position, as it is the case in boost mode, for example? This would allow the target temperature to be reached in a shorter time.
Due to the low flow temperature, it would certainly not be necessary to have so many ON-OFF cycles as for a high temperature heating unit.
Finally, here are two images.