Hello, You TPI coefficient are very, very too high. Is that normal ? Normal values are 0.6 and 0.01. |
2 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
Hello everyone,
I am using Versatile Thermostat for centralized control of my heating system. I have set up 9 Avatto TRVs on radiators across 8 different rooms. The Avatto TRVs do not have valve position control (duty cycle); they only accept target setpoints. A master thermostat entity manages the central boiler. I have configured different modes (eco, comfort, boost) for each TRV.
My TPI Central Configuration is:
coef_int: 2
coef_ext: 0.6
minimum activation delay: 180s
Self-regulation on each TRV: Medium
Internal Temperature of the Underlying Equipment: true
I have a few questions regarding the system performance and observed behaviors:
Any advice or insight into these issues would be greatly appreciated.